Main vent
James W.Stamo
Member Posts: 28
There is no main vent in my friend's house (one pipe steam system).There is no room to make an opening before the elbow and install the main vent. I've seen one where they installed the vent about 6 inches below the elbow of the main pipe, is that ok?
0
Comments
-
That should work
but keep it as close to the elbow as you can so water rising in the "A" dimension won't flood the vent.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -