Is there such a thing as a reducing steam 45?
Tim Gardner
Member Posts: 183
Is there such a thing as a reducing 45 steam fitting from 1 1/2 to 1 1/4? If not, is it bad form to use a 1 1/2 to 1 1/4 black malleable bushing on a 1 1/2 steam 45?
Thanks in advance.
Thanks in advance.
0
Comments
-
Depends
if the condensate flows from the larger pipe to the smaller, you need an eccentric bushing or reducer coupling to keep water from accumulating. If it flows from the smaller to the larger pipe, an ordinary bushing or reducer works fine.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
The condensate is to flow into the bigger pipe, so that's not the issue. I'm afraid the question is simpler and dumber than that: do plumbing supply stores sell reducing 45's and if not, can I mix a black malleable bushing with a steam 45?
Thanks,
Tim0 -
The bushing should work fine
I've used them, never had a problem.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
cool. Thanks again.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements