One pipe steam radiator leaks

I have a single pipe steam system in my home. Recently I noticed water leaking from the ceiling in my living room. I found out that the radiator in the upstairs bedroom is leaking on the bottom at two of the four seams. Does anyone have a diagram of what the radiator looks like? I don't know if it can be repaired or not, I'm thinking probably not, but a diagram would be helpful.

Comments

  • Paul_11
    Paul_11 Member Posts: 210
    REPLACE IT

    if the radiator itself is leaking you should replace it.
    Look the radiator over carefully to make sure it isn't the rad valve or air release valve spitting and it only appears that it is the radiator itself.
    paul

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    Since 1990, I have made steam systems quiet, comfortable, and efficient. We provide comfort while saving the planet.
    NYC RETROFIT ACCELERATOR QUALIFIED SERVICE PROVIDER

    A REAL GOOD PLUMBER, INC
    NYC LMP: 1307
    O:212-505-1837
    M:917-939-0593
  • Steamhead
    Steamhead Member Posts: 17,426
    If it's just a bad push-nipple

    the radiator can be taken apart and the nipple replaced. But you don't want to do this yourself! Hire someone who has done this before, you'll be glad you did.

    If a section has cracked, it's best to replace the radiator.

    This begs the question: Why did the radiator fail? A frequent cause in one-pipe steam is acid condensate, which can be caused by improper venting of air from the system. Check your main vents- are they sized properly (measure length & diameter of your mains & tell us what vents are on them) and are they working?

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Don Bartz
    Don Bartz Member Posts: 5


    Thanks Paul & Steamhead,
    My house is 110 years old. The boiler is about 25 years old. It's an old Weil-Mclain boiler. Everything has worked up til now. I will check into the exact place where the leak is coming from. The first two bottom seams look rusty. That is why I thought it was leaking there.