Frostproof Hydronic System
Jack, CVMS
Member Posts: 81
First, let me point out that my perspective is that of someone living in a part of Alaska with temperatures similar to those in Fairbanks, so make suitable adjustments for your area..
We fill most systems with a 35% mix of Dowfrost (95% inhibited propylene glycol) and 65% deionized water. This provides freeze (slushing) protection to 4° F, and burst protection to -60°F. If we know a home will be shut down for the winter season, we will use a stronger solution, but for over 90% of the homes, the 35% solution is fine.
Rather than attempt to compute the system capacity, we mix the solution beforehand and, after draining and blowing out as much as possible from the system, we pump in the new solution. In an older system, we will usually install a cleaner a week or so ahead of time so that the system will be in good shape for the new solution. Naturally, it is flushed thoroughly before the glycol solution is installed. In addition, since there is always a little residual water left in the system after blowing it out, we "sweeten" the solution with a gallon or so of pure Dowfrost, and check the final results with a refractometer after it has circulated for a while.
We fill most systems with a 35% mix of Dowfrost (95% inhibited propylene glycol) and 65% deionized water. This provides freeze (slushing) protection to 4° F, and burst protection to -60°F. If we know a home will be shut down for the winter season, we will use a stronger solution, but for over 90% of the homes, the 35% solution is fine.
Rather than attempt to compute the system capacity, we mix the solution beforehand and, after draining and blowing out as much as possible from the system, we pump in the new solution. In an older system, we will usually install a cleaner a week or so ahead of time so that the system will be in good shape for the new solution. Naturally, it is flushed thoroughly before the glycol solution is installed. In addition, since there is always a little residual water left in the system after blowing it out, we "sweeten" the solution with a gallon or so of pure Dowfrost, and check the final results with a refractometer after it has circulated for a while.
0
Comments
-
Frostproof Hydronic System
I am instaling a boiler/baseboard hydronic heating system, the boiler is in the garage of a ranch style one level home. I need to add an anti-freeze solution to the heating system........any ideas out there as how I might go about this ?0 -
0
-
Frostproof Heating system
Thanks Mark, appreciate the input.....the article was very informative!! We got the anti-freeze solution into the system very easily and it worked great!!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements