Steam boiler shuts off on low water after 48 hours
Joshua Hosseinof
Member Posts: 8
Our Weil-Mclain EG-45-PI steam heat boiler has this season started to run out of water after only 48 hours when the heat is on.
I've had our plumber and a steam heating specialist come and look at it and they both say that the boiler itself looks ok (it was installed in 1987).
I also did a check by turning off the heat for two days, overfilling the boiler to the top, and then checking after two days, and there was no water leakage at all. So it only loses water when the heat is running. It's a gas heat boiler if that matters.
I've looked at the very useful "Steam Problems?" Q&A section on the site.
The steam heating specialist who came in said that as the boiler itself looks to be ok, the next step is to replace the air vents that are old.
If that still doesn't fix it, he said the next step is use pressure gauges on each of the radiators to try and isolate the problem.
Would it help to narrow down this problem if I shut off individual radiators, one or two at a time and then see if that points to a particular radiator?
Also, how can I tell where the return line is? I believe my radiators have only one-pipe.
Thanks
I've had our plumber and a steam heating specialist come and look at it and they both say that the boiler itself looks ok (it was installed in 1987).
I also did a check by turning off the heat for two days, overfilling the boiler to the top, and then checking after two days, and there was no water leakage at all. So it only loses water when the heat is running. It's a gas heat boiler if that matters.
I've looked at the very useful "Steam Problems?" Q&A section on the site.
The steam heating specialist who came in said that as the boiler itself looks to be ok, the next step is to replace the air vents that are old.
If that still doesn't fix it, he said the next step is use pressure gauges on each of the radiators to try and isolate the problem.
Would it help to narrow down this problem if I shut off individual radiators, one or two at a time and then see if that points to a particular radiator?
Also, how can I tell where the return line is? I believe my radiators have only one-pipe.
Thanks
0
Comments
-
low water
One-pipe steam uses the one pipe for both steam and returning condensate. If you find no water or steam leaks in the boiler or the piping, the next likely culprits are the radiators, radiator valve stem packing, and the vents, which may not be closing when the steam arrives.
You need to inspect each component carefully, and ensure that each radiator valve is fully open. Tell us what you find.0 -
Also
Make sure you check the end-of-main vent as well.0 -
And
look to see if any return lines are buried. If they are I'll bet they're leaking.
Also, if you see a white plume of vapor coming out of the chimney while the boiler is running, it's coming from a leak in the boiler. Sometimes these leaks only occur if the boiler is hot.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements