Why do Raypak boilers pump away?
I thought the same as you have sugested
*What would you think the MFG will say IF I pipe it primary/secondary like I originally thought to do when I looked at this botched installation?
Attached is how it stands today.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=296&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
*What would you think the MFG will say IF I pipe it primary/secondary like I originally thought to do when I looked at this botched installation?
Attached is how it stands today.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=296&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
Seems strange
*Seems strange to me that Raypak's residential boilers come preassembled with a Taco circulator on the return side of their boiler.
*This normally doesn't bother me. I thought I would just move it to the other side Pumping Away. However, this boiler (H-30090R) has a 3/8" copper bypass that attaches the boiler manifold to the suction side of the circulator. It's there to protect the boiler. This copper fin boiler can withstand return water temperatures down to 105ºF. I like that because it's hooked up to a high mass radiant slab.
*The Factory sent me out a piping diagram showing their circulator pumping INTO the boiler's return. The near boiler piping shows an air elimination device "Air Scoop" and expansion tank on the return(between the circ's suction side & the heating load. Strangely enough, they've got an air vent shown not only ontop of the "air scoop", but ANOTHER one in between the air scoop and the circulator. WHOA? They show the feed water valve downstream of "air scoop" This is Raypak diagram Fig. 8898.1 for those of you with the book.
*Could someone tell me how to appropriately pipe this thing. I'm wanting to tear most of it out and start from scratch but, I know these things can be forgiving and the factory bypass stands in the way of me using a pumping away configuration. What am I missing here?
Oh, If you're online you might be able to catch up & talk live w/ me on AIM. I'm Radiantfloors
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
They probably want
They probably want the HX to be under as much system pressure as possible to keep it from flashing into steam. This scenario is possible when pumping away from the boiler due to the negative pressure generated by the circ. Especially true when using high flow pumps which are often found on low mass or tube type boilers. I'd still put the expansion tank upstream of the circulator whether it's on the in or out side of the boiler.0 -
You really
to primary secondary low mass copper boilers. They need a lot of flow. As such the circ location really isn't a big deal. Most copper boiler manufactures show pumping towards the boiler.
I'd caution you against trusting that 3/8 bypass to protect that boiler. A cold concrete slab will greatly overpower the ability of that bypass to offer adequate protection.
I've got a barn full of dead copper boilers that attest to the fact they are very uncomfortble at the operating temperatures you mentioned. If you go there, check the HX and entire flue yearly for signs of flue gas condensation. I got a hundred bucks says you see signs of it within a year or two
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Is it possible,
to pump away from the fin tube boiler & ex. tank without using P/S pumping and not risk a steam flash or condensation? Looking for a KISS solution. If not, I'm going to P/S pipe it & fix the rest of the mess the last guy (a fuel provider) made.
*To catch up with me real time, try AIM My user name is: Radiantfloors
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Why not
Just meet the flow requirements and delta T across the HX. Actually those small ones really don't have huge pressure drop.
I've done them several ways. Sometimes I have made the primary loop, the boiler. As such the "loop" is only a couple feet long. So really the pump location is where?? Pumping away or towards?
Or you could have a seperate primary loop and the boiler pumps into it, now it is a secondary. In that mode the pump really needs to be sized to the boiler spec as the piping is generally not an issue.
The two big issues are flow through the boiler, and adequate return water temperature protection. The piping alone will not always provide adequate protection. Copper tube boilers hate going at it unprotected!
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Here is a little cast boiler
That I will use to replace a hot water heater radiant. I will T-drill a Grundfos MixiMiser into that nude copper section.
Gonna try running a 50 degree delta T (135-185) controlled by the RTI setpoint control, on the boiler to help handle short cycling on this 3 zone system.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
now I've really seen it all ....
in a boiler room ...a toilet! I would pri/sec. it...that way you are sure.kpc0 -
is that a ...
007 on that? looks bigger..kpc0 -
Thats Right! Toilet in mechanical room.
WARNING: Methane gas can be dangerously combustable if flame present;-)
Watch your boiler work as you go.
PEX manifold doubles as toilet paper holder.
I don't think that meets the plumbing & fuel gas code unless it's sealed combustion.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
does that help...
warm the seat on those frosty mornings? Carpet near the boiler? Hmmm...I can see a lot of thing going wrong here...kpc0 -
They're likely geting a New Vitodens
The atmospheric boiler's gotta go.
* Anyone looking for a Raypak Residential 64,000 BTU I=B=R Finn-tube boiler? Low... Low... miles. Look for it soon below W/ Dan's approval of course.
*To catch up with me real time, try AIM. User name: Radiantfloors
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements