Buderus people......JohnNY

JohnNY
JohnNY Member Posts: 3,292
I'm taking over a job in a home just built for a young celebrity couple in my neighborhood. The engineer spec'd a Buderus 334-73 (? I'm going by memory here) with the 2107 Logamatic. I installed the 242 two-stage card and everything is fine.

Is there anything I should know about programming the Logamatic that isn't obvious.

Another concern I have is that the house may be underradiated. In fact, I'm sure it is. The boiler water temperature is often very high (170+) at 48 outside-air temp and the rads all are getting flow but the rooms are hard to get above 69 when it drops below 40 outside.

In his efforts to correct this condition, the engineer wants to change BF room sensor to simple Honeywell t'stat with Taco relay. I know what you're all thinking, believe me, but no one wants to listen to the plumber. Anyway it's his system. I have to play by the rules.

I've never made this switch. Is it easily done?

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=290&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes

Comments

  • joe_14
    joe_14 Member Posts: 138
    buderus


    hi john.
    call buderus they have a very good tech support dept. they also offer classes on logmatic, very good class i have been.
    there number is 1 800 buderus.


    joe.g
  • Steve Ebels
    Steve Ebels Member Posts: 904
    The first question

    The first question I would ask him is how thinks this will help. I mean the water temp is already at 170*s so there's not a lot of headroom above it temp-wise. Does he think the stat is going to magically produce higher water temps or make that 300K boiler produce more than it's rating?

    Is the radiation adequate? Might be the Btu's are there but the delivery system is not. You would notice this by observing whether the boiler struggles to reach its setpoint or if it hits the target temp with a fairly short burn time. Long burns would indicate that the boiler is fighting to reach it's target (large load) and a short cycle would indicate that it's playing with the small load it's seeing.

    Sounds like the BF and the 2107 are doing their job shifting water temps up to meet demand so I don't think there's a problem there. 170* at 40* outdoor is awfully high if the radiation is properly sized.

  • Plumbers, Fight Fire W/ Fire

    Engineers W/ Engineers. The new Buderus discussion forum has a wealth of information and you'll hear back dirrectly from the Buderus factory engineers.

    They can answer ANYTHING related to their product line. You should register while your there.

    http://www.buderus.net/forum/forum_topics.asp?FID=3

    *To catch up with me real time, try AIM. User name: Radiantfloors

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • JohnNY
    JohnNY Member Posts: 3,292
    Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
    Consulting & Troubleshooting
    Heating in NYC or NJ.
    Classes
  • Steve Ebels
    Steve Ebels Member Posts: 904
    JohnNY

    What have you found out about the way the boiler operates? Does it easily reach its target temp or does it take a long time to do so?