Can you vent mains too quickly?
Phillip Biston
Member Posts: 41
I have a building with 240 feet of 5 inch mains, from the header it runs into a 15 foot section of 10 inch pipe, then it tee's off in each direction into the 5 inch mains and wraps back around to the boiler, 1 leg 140 feet and the other 100 feet, into 2 hartford loops then into the boiler. It had 1 Hoffman #75 on each leg, I have replaced them with 3 gorton # 2 on each leg. In reading "The Lost Art of Steam Heating" It says to get the air out fast, My question is, did I go too far, or not far enough?
Thanks,
Phillip
Thanks,
Phillip
0
Comments
-
I don't think you overdid it
Those mains should vent in about a minute at a couple ounces pressure, and three Gorton #2s on each will do this for you. You probably could have gotten away with two per main, but the third one will ensure that the mains vent at a slightly lower pressure than the radiators. This will help get the steam to the furthest radiators quickly.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
No!
Don't feel funny, I have a house with 50 feet of 2 1/2" main with a total of 5 Gorton #2s....the faster the air gets out..the faster the steam gets where it needs to go. Radiators, however, can be vented too quickly which can cause spitting...a good ol' Hoffman #40 will do the trick. MD
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements