burnham boiler and field controls
bob young
Member Posts: 2,177
is this your own personal residence??? you sound like a man with some extra large balls who loves danger. is it a farm??
Burnham boilers and Field Controls
I just converted a Burnham standing pilot gas boiler to electronic ignition. Iam trying to wire in a Field Controls CAS4 and PV300 power venter i cannot figure out the low voltage wiring the latest Field Controls wiring book does not show the Honeywell smart valve i have called tech support and local reps to no avail has anyone done a converstion like this the boiler was a model 206ncl-tei2 its now a model 206ni has a Honeywell smart valve and a Honeywell s8610m ignition module also can i replace the smokepipe from 7inch to 4 in do i need the draft regulater or just the motorized draft damper
rural installation
is this your own personal residence??? you sound like a man with some extra large balls who loves danger. is it a farm??0 -
burnham boilers and power venters
no its not my own house im a heating contracter this is a customers house hes renovating the house and the chimney is going to be removed in the near future by the way its not in a rural area its in winchester ma. near boston
Ed
Why do you have both a Honeywell Smart Valve and an S8610 Ignition Module? If you have a hot surface ignition pilot assembly, then use the Smart Valve. If you have a Spark Ignition pilot assembly, then you will use the S8610M, but you will also need a redundant gas valve, not a Smart Valve. Did you obtain this conversion kit through a Burnham distributor? Let me know exactly what you have and I will be glad to help.
Glenn Stanton
Burnham Hydronics0 -
burnham boiler and power vents
i purchased the conversion kit thru a local supply house it was shipped directly from the factory has a honeywell s8610 ignition module and a honeywell vr8204c gas valve with 3 plugs marked pv ,pv/mv, mv
That kinda talk
won't last around here long Bobby.
Clean it up or take it someplace else.
Mark H
Conversion Kit
OK....now that I know you do indeed have the correct gas valve, I can proceed. I will have to look up the power venter and control kit and will send you an e-mail with the directions. The gas valve you have is not a Smart Valve.
Glenn0 -
Thanks for handling this one, Glenn. nm
Glenn.....You be sure to e-mail me a copy of that wiring diagram,ya hear. There is something I use only about three times a year but would be nice to have in the archives.0 -
I have a Burham model 206NCL-TEi2 boiler and would like to add boiler reset control. Is this possible with this model?0
The unanswered question is do you need a Field barometric and the answer is YES! The venter will pull too much air through the boiler and drafthood and could create a dangerous condition. The motorized damper is no longer needed.
This installation must be tested with a combustion analyzer to confirm all the gases are being pulled out of the boiler, not just the room.
- 85.2K THE MAIN WALL
- 55 Biomass
- 73 Chimneys & Flues
- 130 Geothermal
- 3.3K Oil Heating
- 61 Pipe Deterioration
- 885 Plumbing
- 5.9K Radiant Heating
- 376 Solar
- 14.7K Strictly Steam
- 59 Water Quality
- 49 Industry Classes
- 89 Job Opportunities
- 28 Recall Announcements
