Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Main Venting

ken best
ken best Member Posts: 2
one is 2.5in dia 39ft
two is 2.5in dia 49ft

Comments

  • Steamhead
    Steamhead Member Posts: 17,375
    Vent sizes

    I'd put two Gorton #1 or Hoffman #75 vents on the short main, and a Gorton #2 on the long one. The Hoffman #4A is too small for either one.

    You want to fill the mains completely with steam in about a minute. These vents will do that.

    The Gorton #2 is the largest vent made today. If you can't find this vent in your area, go to

    www.gorton-valves.com

    or call Gorton at 908-276-1323. Talk to Ken Kunz and tell him I sent you.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting