Check Valve Noise
Justin Gavin
Member Posts: 129
I have installed a Munchkin as per the O & M manual on a job. I put the boiler circ pump on the return side as stated in the installation guide. I installed a Grundfos UP 26-64 and have a noisy check valve. Does anyone have any advice on how to correct the noise problem. I installed a Danfoss Pressure Diff. Reg as per the installation manual and it too made noise at first but currently no longer makes any noise.
Right now I am running temp heat to 2 hot water coils. I have 4 more zone valves to supply to when I get the baseboard installed.
I appreciate your help in this matter.
Thanks,
Justin
Did I do something wrong? Please let me know because I have a feeling the owner will not want to deal with the noise and I don't think he should have to.
Right now I am running temp heat to 2 hot water coils. I have 4 more zone valves to supply to when I get the baseboard installed.
I appreciate your help in this matter.
Thanks,
Justin
Did I do something wrong? Please let me know because I have a feeling the owner will not want to deal with the noise and I don't think he should have to.
0
Comments
-
The check valve is likely
too big. Line size check valves often chatter because the fluid velocity is not high enough to keep the valve fully open.0 -
flo-control
wow about a flow control [b & g or taco ] in lieu of a conventional check. they are pretty much silent.0 -
I would also recommend at least 12 pipe diameters of straight pipe upstream of the check valve to reduce inlet turbulence. I've found this works well with spring-loaded checks.
Siggy0 -
For further Refrence
Thanks for the info but I guess my next question is this. If I can't offer 12 pipe diameters of betweent the discharge of the pump and the check valve what should I do? Install a flow control valve?
I have attended a radiant class a last week and they were talking about a heat trap. I liked the idea but kinda fuzzy on the exact requirements and design. Any rules of thumb or advice would greatly be appreciated.
Thanks Siggy
PS. I have the first addition of your book and have ordered the second edition just yesterday. What a coincedence.
0 -
Ideally
the check would be sized and installed in such a way it doesn't have a chance to make noise.
If only we lived in a perfect hydronic world
A couple other thoughts. Can you fit a Grundfos 15-58 on, speed 3, into the 26-64's place. Check the curve on the 15-58, it gets close to the 26-64. The 15-58 would give you a pump with a "quiet" intergral check.
Hey Grundfos, when will we see the 3 speed, intergral check 26 series circs.????
Or replace the check with one of the various soft seat, low pop pressure models. This would soften the noise, and the low pop spring may make the issue disappear altogether.
Conbraco, for one, offers soft seat checks with various spring choices.
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Thanks for the info
Well I have a 26-64 in place with a soldered check valve in. I will probably remove it and place a 58 in. I should be OK. I am just kicking myself because I already placed the same check valves in 3 other spots that I havn't started up yet and now I will probably replace them.
The problem is that I used Pro-Press fittings and they are quite expensive to be throwing out. Oh well. A valuable lesson learned here.
Thanks to everyone for their help.
Thanks,
Justin0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements