pilot out

Steve-O
Steve-O Member Posts: 21
Have a Weil McLain cg-7 standing pilot natural gas boiler installed two months ago.Got the call the other day.... no heat...great!Pilot out for now re lit it but I know it will be back to haunt me real soon .What steps should I take to trouble shoot this so it doesnt haunt me any suggestion would really help . thanks

Comments

  • Steps for Pilot out

    I gave some info on Tips for Winter post which I will put back up for you.

    In addition to those you need to take some millivolt readings:

    Open circuit should be between 25 to 35 millivolts no less than 17 to 18 if less clean the pilot or replace thermocouple.

    Closed Circuit should be roughly half of the open circuit or about 15 millivolts.

    Then bring the burner on and watch the meter the readings should remain steady maybe up or down a millivolt or two but no more.

    Then blow the pilot out the magnet should drop out with an audible click at less than 6 millivolts. If more than that the valve will need to be replaced.

    The other things to look for is lack of combustion air in the room and poor draft which should be resolved by conducting a combustion analysis and Carbon Monoxide test on the equipment to determine if it is burning correctly.
  • pat_5
    pat_5 Member Posts: 3
    gas pressure

    you may want to check the gas pressure at the valve, i performed a service call last fall, pilot kept going out. i relit the pilot, sounded noisy, lift off, checked gas pressure, it was high 8.5" w.c. for nat gas. reduced to 4-4.5 and haven't had a call back. good luck
  • How did you reduce

    the pressure to the pilot?
  • Tony Gatto
    Tony Gatto Member Posts: 2
    pilot

    Most gas valves have a adjustment for the pilot. But the problem was more likely the draft produced by the high gas pressure when the valve kicked on, and blew the pilot out or pulled it out.


    tony
  • I ask that question

    because combination gas valves do not regulate pilot gas. The regulator in the gas valve will regulate main burner pressure only. The pilot adjustment screw does not adjust pressure but adjusts flow, it is simply a throttling screw.
  • ken D
    ken D Member Posts: 60
    pilot out

    Friend of mine got a service call, and a window was left open and when he went in to check the pilot assembly for proper hight, etc., he felt the draft from the window. Would blow the pilot out.