counter flow loop off standard steam system
clammy
Member Posts: 3,163
have a job with a standard 1 pipe steam main condensate flow in thew same direction of flow as the steam but here's the kicker there's a drop down into a wet return but before it is below the water level about 6 inch below the steam main there's a tee with a counter flow branch it picks up 4 rads it originally was a counter flow but made alot of noise and didn't heat well some one tryed to drip the end of it's main and still no improvement i was going to re pitch it back to the counter 1 inch per ft. get rid of the drip return my big question is should the end of this counter flow main have a steam vent on it or let the rads vents do the work.and if it does get a venrt shoulkd it be installed 8 to 10 inches before the end of the main. thanks for any input
R.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating
0
Comments
-
The Vent for that entire main
should be near the end of the counterflow section. But before you install it, see if the pipe is big enough for the radiation. Counterflow mains must be one size larger than parallel-flow mains for the same radiation load. This allows the steam and the water to keep out of each other's way, preventing banging.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
pipe size
this was a pre existing condition i'm just trying to straighten it out and get rid of the banging but as i think about it is probaly to small and is not insulated going with insulation later this week and ,re pitching and installing new vents going with gorton first time on the mains hopefully the supply house still has them just got brought up by another company so all the good stuff going and all the garbage is coming in no more taco slant fin and probaly no gorton they switch to selling garbage and tell you it's great bigger mark up garbage and more money in there pockets i hate it but it happen around here all the time it sucks thanks steamheadR.A. Calmbacher L.L.C. HVAC
NJ Master HVAC Lic.
Mahwah, NJ
Specializing in steam and hydronic heating0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 918 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements