peerless steamer problem

steve_6
steve_6 Member Posts: 243
Has anyone had any problems with peerless steam boilers running out of water during their steam cycle. I have a 6106 thats been in place since May that keeps going off on low water. The returns are clear and condensate seems to be coming back ok. The boiler matches the connected load. thanks.....

Comments

  • bigugh_4
    bigugh_4 Member Posts: 406
    If ya ain't able

    to account for the loss of water, it my be going up the chimney! A cracked boiler above the water line is the culprit. Look at the chimney top, and see if there is a load of steam coming from it. Good luck
  • me thinks

    you'll need joe's equalized tank...i will dig up his instructions...
  • steve_6
    steve_6 Member Posts: 243
    don't think thats the problem

    It's a brand new boiler. No steam coming from the chimney
  • steve_6
    steve_6 Member Posts: 243
    equalizing tank

    gerr can you post it on here
  • steve_6
    steve_6 Member Posts: 243
    here are a couple of pictures

    this is in a Mouat vapor system.
  • Steamhead
    Steamhead Member Posts: 17,358
    Is there anything about the system

    that would cause that Peerless to generate more steam than usual, such as uninsulated pipes or bad or missing main vents, or the pressuretrol set too high?

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • steve_6
    steve_6 Member Posts: 243
    steamhead....not really

    mains are insulated, 3 Gorton # 2's for venting, and vaporstat set with the main @ 4 and the differential @ 2ozs.
  • Steamhead
    Steamhead Member Posts: 17,358
    It may be dirty

    in which case it's generating wet steam, which uses up more water. Try cleaning it.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Scott G.
    Scott G. Member Posts: 15
    Ahh Yes...

    I had a steamer do that same thing to me 2 years back. Piped to specs. Insulated well, the works! She would steam and slowly go off on low water. I followed Dan's advice and "Got out of the boiler room"... What I found was a clevis hanger that was removed, causing a VERY slight sag in the steam main. Reconnection of that hanger, made that ol' girl purr liked a horney 18 year old! GOOD LUCK...STG
  • Yes

    It doesn't happen often to us , but it does happen . It will be running for steam for a while , just a little water in the sight glass , then poof - all gone . Could be like Steamhead said - wet steam leaving the boiler , especially on a new install . If memory serves me , theres only 5 or 6 inches of height before the Hartford Loop with the 61 series ( I think they were the G series when I used to install em ) . Not much water content at all .

    Very nice install Steve .
  • Bob_19
    Bob_19 Member Posts: 94
    Pending

    any leaks that may show up is the boiler possibly trying to make more steam than it's set for per/hr and the feedwater makeup can't keep up before going off on low water.
    Are you experiencing heating issues?

    Not only should the original problem be solved I would start to wonder if the city makeup is even trying to keep up, and also why the condensate may not be returning quick enough.
    The eternal question, "where is it all going"
  • steve_6
    steve_6 Member Posts: 243
    no leaks in the system

    the system has 490 sq. ft. edr .boiler was originally over fired from the factory by 25,000 btu's . we corrected that. boiler was skimmed 3 different times, totalling about 8 hours of skim time. also measured 3.5 gallons of boiler water from the normal water line to the low water cut off line. all the water does come back to the boiler