two different systems in 2 pipe steam system
Pat A
Member Posts: 4
0
Comments
-
Radiators don't push out air, won't heat
Have 2 systems, original Richardson with 10 radiators, mixed with 3 add-ons with steam traps(just maintained). Problem is upstairs Richardson won't heat(steam gets to it but won't fill(disconnected radiator, it is not blocked), checked ball trap, seems ok, downstairs radiator add-on, same problem. Just added Gorton #1 and #2(replaced old Trane vacuum type) vents. Any ideas?0 -
I'll bet
you'll find there's a problem with the dry return. The air vents thru the water-seal unit ("ball-trap") or thermostatic trap and back thru the dry return to the main vent in the boiler room. If that part of the dry return dips down and accumulates water, the air from the radiators cannot get by.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements