Series Loop

bigugh_4
bigugh_4 Member Posts: 406
Your system is limited to how much water can be pushed through those 1/2" lines. if you need more you will be cold! that given, a monoflo tee would help in that situation. First, start out with a proper heat loss calculation. then design from there a system that will work. Nothing beats the cold like doing heating correctly!

Comments

  • Robert O'Connor_3
    Robert O'Connor_3 Member Posts: 272
    Kickspace Heater

    I just had new baseboard heating system installed.The heating contractor installed 3/4" baseboard. 2/3 of the loop is 3/4" until he hits the kickspace heater it is reduced to 1/2" and the last 1/3 of the loop is feed with 1/2". Also on the last baseboard it is feed with the 1/2" and the return to boiler is 3/4". He said it is a series loop system. Is this ok to do?
  • Steamhead
    Steamhead Member Posts: 17,495
    Another way

    is to bypass the kicker with 1/2" pipe. This way half the flow goes thru the kicker and the other half bypasses it, and the rest of the loop gets the full flow of a 3/4" pipe.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting