Flame roll-out too sensitive
techheat_2
Member Posts: 117
a bad roll-out switch. By even asking if a vital safety control can be bypassed I assume you are an HO. You really need a Pro to handle this
0
Comments
-
Over sensitive flame roll-out switch
Heating season begins. Buderus G124x32 gas boiler works fine. Then, after a warm spell ,it fails to fire. Damper is open, circulator is hunning away pumping cold water. So, I wiggle the sort of loose red button in the flame roll-out switch , and, Hey!, i get ignition. I think it did this once last Fall too. The 31 foot stack of cold air in the 6 inch aluminum chimney liner must hold back the vent gasses till it is warmer. It is a new , clean liner we installed a year ago.
Question: can I jump the switch with a little piece of wire till the heating season is in full swing?? Other solution.??
0 -
Nope!!!!
That switch is there to keep you and yours alive my friend. Do Not Jump It!! Get an exact replacement and try it. It may just be a bad switch. Check your house for exhaust fans that may be running, dryer, bath fans, kitchen fans etc. That spill switch should not trip under the conditions you describe with your chimney. It takes a minute or two at least. Watch it when it fires if you can to see if you are actually getting flue gas out of the draft hood. I have a hunch that something is pulling your house into a negative (less than atmospheric) pressure. Again, please don't bypass or disconnect that spill switch!!0 -
Roger that.
Thanks Steve. No, I would not disable it without checking with a pro first. . To locate and define the cause and ask about it all indicate my reasoned caution.
You are probably correct about negative pressure. There is a vented drier and an independently vented water heater in the 12' by 24' basement room.[ Cannot recall if the drier was in use.] There is a hinged basement window open 1/2 inch for makeup air, to approximate the area of the 6 inch vent. Nonetheless, the whole house leaks some and there are 3 firplaces whose dampers are not perfectly tight.
I'l order a new switch and give it a try. Will probably add a Tjernland inforcer or something like it in future. As stated, this has only occurred at the start of the heat season.
Thanks to all at this site.0 -
Fireplaces
No gas device in the house wins against a fireplace. If you had one of the fireplaces running when the boiler tried to start the downdraft from the fireplace would keep the boiler from venting.0 -
this thread makes me think of what I just heard
Through the grapevine.I hear that some guys don't pull permits in my fathers town because he enforces make up air
they think he's picking on them. go figure?0 -
I've had quirky roll-out switches before...intermittent problems
But either way, get a pro in there to diagnose and fix. Its nice that you know, but leave the actual work to us. Mad Dog
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
I gather pop's is the inspexctor? good for him shame on them
He's doing the right thing. Mad Dog
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
correction
In starting this thread I erroneously called it the roll-out. It is the spill switch in question, as Steve correctly recognised.. Restated, the device on the low edge of the draft hood.
We crack a window or door when using the fireplace. There are wall and chimney vents for near or in the fireplace...but it's not first on the honey-do list. Opening the outside ash pit door [not good] produces an undesirable blast furnace effect , not so cheery [or safe]as a calm wood fire, but probably useful to heat iron bars for blacksmithing. But we digress..0 -
make up air
Have a fresh air intake, properly sized, installed into that room. Partially open windows that wind, water, debris or rodents or luck can close or invade your house through, are a poor substitute for a properly sized air intake. Is your families safety worth the risk. Think CARBON MONIXIDE. A draft fan like a Therlund exhaust venter is not the answer to a makeup air problem0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements