Steam tee
Steamhead
Member Posts: 17,387
it was wrong then and it's wrong now. Unless you're describing a "double elbow" rather than a regular tee- but if it looks like a regular tee, you should remove it and use two risers from the header.
Remember that a new boiler will make steam a lot faster than that old snowman, and this will aggravate any piping problems.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
Remember that a new boiler will make steam a lot faster than that old snowman, and this will aggravate any piping problems.
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=157&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting
0
Comments
-
I am about to ....
do a stem boiler replacement job in a home. The old boiler is a old "snowman" coal fired that was converted to oil ,then gas. I will replce it w/ a Smith GB200 series gas boiler. On the old boiler the supply comes out of the boiler and then enters a tee that is bullheaded...it has always been that way...for a hundred years ...and never a problem. How can this be? CAN I leave it that way or should I break into the main and replace it w/ 2 90's. I would like to save myself the work but....kpc0 -
As usual steamhead is correct....................I'd say that
maybe only 3-4% of steam boilers we do have salvageable headers. Especially with the low water content- fast steaming new boilers, a nice big fat header is called for. On smaller steam boilers I will either use a 2 1/2" header using both tappings OR a 3" header using one tapping. Bigger boilers always get a 3" header. Mad Dog
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Speaking from experience.....
I'm going with the boys on this one. Your changing from a perkolator to a cappicino machine, and the speed at which the steam is being produced is FAR faster.That bullhead will bite you in the butt. Make a smooth and equal transition to both feeds and you'll be much better off. Chris0 -
Great anaolgy Chris ...you a funny man
mad dog
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
OK...
that is what I thought the answer would be...I have never heard of the double elbow before...I'll check but probably a tee. I'l get some pictures to prove I did the right thing. kpc0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements