Indirect heater question

newbie
newbie Member Posts: 5
The specs say my Weil-Mclain indirect heater looses "less than 1/2°F per hour." So why does my boiler cycle on and off every 15 minutes or so in the summer when no other zone is calling for heat? If my solution is to replace the OEM tank thermostat with one where the upper and lower temperature limits can be adjusted, does anyone know who sells one. Thanks.

Comments

  • newbie
    newbie Member Posts: 5
    Indirect water heater

    The specs say my Weil-Mclain indirect heater looses "less than 1/2°F per hour." So why does my boiler cycle on and off every 15 minutes or so in the summer when no other zone is calling for heat? If my solution is to replace the OEM tank thermostat with one where the upper and lower temperature limits can be adjusted, does anyone know who sells one. Thanks.
  • hot_rod
    hot_rod Member Posts: 23,400
    I question the same

    wonder where that number comes from? Seems all tank manufactures quote the exact number! Maybe they rate them in a 100 degree ambient room :)

    You could have ghost flow or heat migrating into heating zones. Also piping loss around the boiler and tank. Does it have a DHW recirc system? If so, is it insulated and on a timer and or aquastat?

    If the 1/2 degree figure were indeed accurate then 4 degrees in eight hours? That shouldn't even trip the aquastat for another boiler cycle.

    Is you boiler set to maintain temperature, or only fire on DHW call in the summes?

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • newbie
    newbie Member Posts: 5
    indirect water heater

    There is no thermal syphon at work here. Pipes are insulated and automatic valve shuts off boiler supply water to heater when temperature is reached.
  • jim sokolovic
    jim sokolovic Member Posts: 439
    Indirect water heater tank insulation

    Many brands of these have very good insulation, and the low temperature loss claims are true. Does your boiler have an aquastat that maintains a certain minimum water temperature within the boiler itself, which would turn on the burner even though no hot water is being used?
  • newbie
    newbie Member Posts: 5
    indirect water heater

    But I hear you hotrod on that oft-quoted spec of 1/2 degree loss. I, too, see that everywhere.
  • newbie
    newbie Member Posts: 5
    Aquastat

    There's a dial to set a high temperature limit on the boiler, which is currently set at 160 degrees. Is that the same thing?
  • Aidan (UK)
    Aidan (UK) Member Posts: 290
    thermostat

    The boiler is cycling on & off under the control of it's thermostat as it cools down. It's probably losing heat up the flue. Either the tank thermostat is defective or the boiler is being turned off by it's thermostat before the tank thermostat reaches it's setpoint. What temperature is the tank set at?

    The tank (cylinder) thermostats are usually strap-on devices over here. My one reaches 60degC and the boiler shuts down for 10 hours or more, or until someone uses the hot water, assuming the kids haven't left the taps running. The tank thermostat is interlocked with the boiler, so the boiler doesn't fire unless there's a demand.

    http://content.honeywell.com/uk/homes/Catalogue/Heating Controls/2.9 L641.pdf
  • kevin coppinger_4
    kevin coppinger_4 Member Posts: 2,124
    the boiler is....

    set up as a tankless...you could replace the honeywell 8124 w/ a 8148. that will set it as a cold start and only fire when there is a call for heat. The other option is to turn down the setting to say 140. kpc