Single pipe parrallel to single pip counter flow
Ed_9
Member Posts: 2
Was wondering if I can do this. I want to finish my basement and the return side sits lower than the supply side and takes up some much needed headroom. Just curious before I call someone in. Would it be possible to just cap the end of the main run and vent it (of course make sure it's pitched back properly)?
0
Comments
-
If you increase it's size you can
otherwise there isn't room for the condensate.
Noel0 -
There's more to it than that
You would need to install a new main that is one pipe size larger. The existing main was not sized to allow condensate to flow back against the steam.
A better solution might be a "rise and drip" where the level of the main is raised, and the low point gets a new "drip" line to drain any condensate that might accumulate there.
This is a job for a pro. Go to the "find a Contractor" page of this site to locate one near you.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements