Y-strainer screens
Luke Lefever
Member Posts: 62
I can't speak for Munchkin, but NTI Trinity uses a similar heat exchanger... local manufacturers rep suggests that the NTI be installed with a water to water heat exchanger to keep the silt out of the boiler. I asked about Y strainers, and he said no, not recommended. Better talk to Munchkin.
0
Comments
-
Y-strainer screens
Plan on adding a Y-strainer to my boiler.
Concerned about clogging up the recent Munchkin (140m) with sediment from my old converted gravity system.
Y-strainer screens are available in a variety of 'mesh sizes'; 20, 40, or 60 (in this case)
20 mesh =0.0340 inch openings
40 mesh= 0.0150
60 mesh= 0.0092
20 mesh adequate for low mass boilers?
Want to stop the crud without significantly impacting the flow. Are Y-strainers really the best solution? Anyone use something else (say, basket strainers?) instead?
Guidance appreciated...0 -
Hate to bump
Hate to be a 'bumper', but some of you MUST use Y-strainers.
Maybe I should have posed the questions differently:
1) Do you put Y-strainers on your returns with old CI systems?
2) How about with low-mass boilers which are somewhat more likely to clog?
3) If so, what is the proper screen size?
Guidance appreciated. Thank you.
0 -
Strainers
There should be nothing wrong with adding a strainer to your piping system as long as you clean your piping system, flush the system, allow for the correct pressure drop the strainer will cause, understand that strainers require cleaning maintenance, add valves for maintenance and possibly add pressure gauges upstream & downstream of the strainer. Read these Keckley links for assistance.
http://www.keckley.com/style_b.htm
http://www.keckley.com/strain6.htm
http://www.keckley.com/strain7.htm
Perforation size will affect pressure drop the same as a clogged strainer will impede flow. I would say if there is not a "maintenance" person available to keep a watch on the system that you would probably want to re-think strainers.0 -
Bill is right
if you, in fact, do have crud in the system you will need to keep an eye on that strainer. Of course the finer the mesh, the more potential for blockage.
I would guess the standard screen is a good compromise for flow and most partical collection.
Ball valves on both sides is an excellent idea for ease of filter removal and cleaning.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Bill is right
if you, in fact, do have crud in the system you will need to keep an eye on that strainer. Of course the finer the mesh, the more potential for blockage.
I would guess the standard screen is a good compromise for flow and most partical collection.
Ball valves on both sides is an excellent idea for ease of filter removal and cleaning.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements