How do we reassemble a peerless 4 section boiler?

frank s
Member Posts: 64
2 men who work for my uncle had to split a 4 section oil boiler in half to get it down a spiral staircase, now for the life of them they can not get the final push nipple seated right, is there a tool or trick to this??? This is an oil fired boiler if that helps.any advice is greatly appreciated as always. Thanks for your knowledge,
Frankie SEV,
P.S. this is a peerless boiler
Frankie SEV,
P.S. this is a peerless boiler
0
Comments
-
I had that happen once
on a commercial Peerless . One of the upper push nipples went in crooked and we had to cut it out and get a new one . That was a 2 hour mistake .
We had to split many a Peerless for similar situations . When we assembled it back together , we would use a soft setting sealant on the push nipples . Peerless uses a white colored sealant , and sometimes I saw Rectorseal #5 in there . The trick that worked for us was to catch the top push nipple first and then wiggle the 2 halves till the bottom push nipple caught . Then you tighten the rods evenly . A last resort is to lay the back section down on the floor and drop the top half in . Good luck to your uncle and crew .0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 940 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements