I need some expansion tank theory help... :-)
hot_rod
hot_rod Member Posts: 26,580
For the how and why's of the charts, try this link. Siggys new software has a great sizer and volume calculator, very handy.
hot rod
http://www.pmmag.com/CDA/ArticleInformation/features/BNP__Features__Item/0,2379,4067,00.html
  • jess askey
    jess askey Member Posts: 11
    Firstly, let me say that over the last 5 years I have found that Dan's site, The Wall and The Lost Art of Steam Heating have been the best site for a DIY'er like me. I appreciate all the help everyone and Dan has given me the few times I post my silly questios here.
    Also, I still have a free 'antique' ARCO coal fired boiler in working condition in Laramie, WY if anyone wants it!!!
    Now to my question...
    Im in the process of pouring a hydronically heated slab for my workshop/pinball room. It is 3/4" tubing and I have approximately 300' in my single loop which to my best calculation is 6.8 gallons of water. Operating temps would be from 55 degrees (F) to 125 degrees. So, how do I size my expansion tank. I realize that the expansion depends on my pressure but that is going to be very low I beleive. I could not find a good water thermal expansion equation anywhere. I was looking at this 'hydronic expansion tank' (http://www.zurn.com/operations/wilkins/pdfs/specsheets/wxt-HXT.pdf) but could someone plese chime in and connect the dots for me. I dont' want a 15 liter tank if I only need a 2 liter inline version. Plus I guess Im a bit unsure of how to actually balance an expansion tank (I will read some instructions that I found however for a quick tutorial) but feel free to edumacate me on that too. ;-) thank you again.
    jess askey
    laramie, WY
  • John@Reliable_4
    John@Reliable_4 Member Posts: 101
    Jess, check this site out............
    http://www.amtrol.com/website/content.nsf
  • Big Ed
    Big Ed Member Posts: 1,117
    Chart
    hope this helps
  • Arthur
    Arthur Member Posts: 216
    Expansion tank
    Water expands at 1/22 from cold to hot. ie If you have 22 galls when cold in your system you will have 23 galls when hot.
    It's always better to have too large a tank than too small. The static pressure in the tank (system empty) should be the pressure you pump the system up to when cold. Then the diaphragm will dilate as the water expands equaliseing pressure on both sides of the diaphragm. Too much rise in pressure cold to hot is usually a sign of a tank which is 1) too small for the system or 2) The tank has lost it's pressure or 3) The system pressure has been set far too high above the tank pressure resulting in the diaphragm being prematurely distended and unable to take the expansion of the system. With the good quality european tank we use over here I've never seen a diaphragm in a tank go yet if properly installed.
  • Mark Eatherton1
    Mark Eatherton1 Member Posts: 2,542
    NZ...
    would that be New Zealand???
    ME
  • jess askey
    Thanks... You guys rock!!!
    Thanks for the links, plenty to keep me busy. Anyone have any opinions on the watts inline expansion tanks (seem to take up much less space)...
    http://www.plumbingworld.com/expansiontankbywatts.html
  • Arthur
    expansion tanks
    Yep. That's New Zealand. That paradise in the south pacific just to the east of Australia.
    Come down and visit us some time.
  • Arthur
    Expansion tanks
    The watts expansion system would be aright on an direct domestic hot water system and could be quite an advantage to help absorb water hammer and expansion of a small cylinder, note it has a water expansion value of 1.15 galls which means it would be ok on a cylinder up to about 30 galls. the pre pressure is far too high for a heating system at a prepressure of 40 PSI.
    A 30 gall cylinder is going to have an expansion of approx 1.25 galls from cold to hot.
    It is obviously designed for a DHWS not a heating system.