Diaphram tank charging

about expansion tanks and read somewhere that you can install a guage close to the water connection of a diaphram tank and adjust your air charge according to that pressure. I've always thought you were supposed to shut and bleed off water pressure before checking the air pressure. Are both ways OK or not??? WW

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=255&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Jerry Boulanger_2
    Jerry Boulanger_2 Member Posts: 111
    There must be no pressure

    on the water side of pre-charged tanks when checking and adjusting the air charge. An extra tip - use oil-free air.