HWS Schematic
Eric
Member Posts: 95
Comments Anyone......
They are concered about thermal shock, Cast iron boilers.
There are several things that seem odd: complexity, bypass in the primary loop, and diverting valves on boilers.
They are concered about thermal shock, Cast iron boilers.
There are several things that seem odd: complexity, bypass in the primary loop, and diverting valves on boilers.
0
Comments
-
looks kinda cool ...hehe0 -
schematic
0 -
schematic
The diverting valves on the boilers are there, I would think, to prevent low boiler return temperatures on start up & fireside/back-end corrosion. That bit looks right.
The thing that looks wrong is the way the heat-exchanger (top, left-of-centre)is piped. I think it's a plate heat exchanger to separate the glycol system from the boiler. These have a relatively high hydraulic resistance, but you'd need another pump, or a regulating valve between the F&R connections, to push the boiler water through the HX. With the existing arrangement, the boiler water will just by-pass the high-resistance HX and flow straight on down the low-resistance primary pipework. I'd query this. I agree with Eric, the glycol loop looks like it's going to stay kinda cool!
I can't read most of the rest of it.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements