RADIATION CONTROL VALVE
Dick_2
Member Posts: 14
our Warren Webster two pipe steam system radiation units(which are recessed in the wall) have a small disc with holes all around on each inlet valve stem. This disc has a small stub which stops the opening of the valve by meeting a post on the valve housing. This disc can be rotated and I just wondered if the purpose was to allow more or less steam into the radiant finned panel?
0
Comments
-
Each stop
on that dial represents 10 square feet of radiation. It causes the valve to act like an orifice. The installer would set the valve for a value that was a bit less than the radiator's rating, thereby assuring that the trap would see nothing but condensate. These valves helped extend the life of the traps.Retired and loving it.0