Thermostatic valves

Mark_7
Member Posts: 123
What piping system works better for radiators with thermostatic valves? Monoflow tee's or parallel feed and return.
0
Comments
-
TRV's
I would say the TRV's would work fine on both systems, however you do need to be aware that the TRV will increase the head (resistance) in the line and could be a problem on some monoflow branches.
Good luck
DWood0 -
TRVs on monoflow
Parallel would be best. As Dennis said, with monoflow you need to watch that you don't create too much pressure drop across the radiator, or you won't get any flow.
Look for a TRV with a high Cv value. Honeywell for example make a V100 series with 2.5 Cv and a V110 series with 4.6 Cv
Mark0 -
Tvs on monoflow piping systems
will not work. Any fitting or device that alters the pressure drop in venturii fittings will come back and bite you on the ------- (radiator).
jake0 -
Buderus provides VERY good information on using TRVs in a single-pipe system with their panels. Monoflow/Venturi and proprietary diverter valves are both discussed.
You just can't shortcut on the calculations and have to stay within established parameters.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements