Hot water heaters and antifreeze
Bruce
Member Posts: 27
Iam building a small hot water radiant floor (concrete) system using a 6 gal.water heater as a boiler.My question is. I will be using propolene glycol 20-25%.Heating elements are copper with a galvinized or zinc coating.Dan's books say this is bad in a system using antifreeze.Is there a reason way they don't just leave them copper? can I remove the plating,or do I go to a s.s element.Thanks Bruce
0
Comments
-
Yank the anode, also
it may react with the glycol, and it is not needed in a closed loop system. (plus it frees up another port for a relief, gauge, air vent, stat well, or whatever)
The inhibitor package in the glycol will handle the small amounts of O2 from the blend water.
Yes, get a stainless or copper element, just to be sure. Chromolox make a wide variety of elements in voltage, wattage and material types.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements