Copper tube vs. cast iron boiler
Stemmer
Member Posts: 4
Good Day.
Take a look at one of the condensing boilers for your application. The Ultra fron Weil McLain should meet your clients wishes, being an aluminum block with water content and will run at low temperature thus no special externial controls, mixing vavles etc. to worry about.
Stemmer
Take a look at one of the condensing boilers for your application. The Ultra fron Weil McLain should meet your clients wishes, being an aluminum block with water content and will run at low temperature thus no special externial controls, mixing vavles etc. to worry about.
Stemmer
0
Comments
-
Copper tube vs. cast iron boiler - What do you think
(Smaller size boilers)
Generally I spec. copper tube because of the speed of response goes along with the contol we usually use.
A client of ours prefers cast iron based on maintenance.?
Now (for this client) I need to spec. a boiler for heat-add to a water source heat pump loop. Tough for me to look at cast iron with the low temp. water (even though I am designing it with secondary pumping with a high proportion of bypass).
Any thoughts?
For extra credit - On water source heat pump projects I design the boiler secondary pump with enough bypass to maintain a high temp. return to the boiler. This is fine for a running system but in practice the boiler will still see low temps when the pump and boiler cycle on. Is there a problem with this???????????0 -
Use a Cast Iron
Boiler with pump logic built into the control, I.E, Buderus or Viessmann. This keeps the pump from running until the water is at a preset temp. Low water temps (<140*) are no problem for either of these brands.0 -
Regardless of cast or copper
you need to be concerned with condensation in the hx and flue pipe. Extended run periods below the fuel dewpoint will cause this, regardless of copper or cast iron construction.
Condensing boilers excepted, of course. These will have aluminum or stainless HX's that are designed to run, happily, below condensing temperatures. We hope!
Copper or cast? Depends on the application. I find the higher mass, larger water content cast best for multi zone, possibly micro load zones, common with todays zoned systems. Less cycling, provided by BTU's stored in the water itself and the mass of iron.
I like the copper for steady consistant loads. Snowmelt, dhw production, maybe connected to a matched air handler, stuff like that.
I'm not convinced copper tube boiler can handle 110 return temperatures continually, as some say, and I have a barn full of 5- 12 year old ones to prove this therory.
Raypak includes a bypass tube and ball valve to handle low return temperatures, to a point. It does not provide boiler protection under all conditions, however.
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements