Steamer - DF
Options
Dan Foley
Member Posts: 1,268
This a two pipe steam system Steve and I are going to rebuild. It is in a school in Silver Spring, MD. The boiler was replaced with two boilers approximately six years ago. They have had nothing but problems since. Note the condensate pump that feeds into both boilers. Both boilers are also connected below the water line. The welded header is not piped to Burnham specs. No one has touched the traps in over ten years according to the school administrator. What else do you see that is wrong? -DF
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=262&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
<A HREF="http://www.heatinghelp.com/getListed.cfm?id=262&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>
0
Comments
-
More...
More Pics. -DF
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Oh My !....
Where to begin ?
I bet there's a good picture of how to do this right in the Burnham manual, and what you've showed isn't there !
WOW . Someone got paid for this !....Oh My ! Chris0 -
Firing
as one or staged? Where's the redundant safeties? Black iron pig tails! Wet steam into system - wrong location on the header for that takeoff!Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements