to look at a boiler replacement tommorrow.Cast radiators on the second floor and the first floor is heated by radiant in the ceiling.How would I do a heat loss for the first floor? Do I assume the dead men that did this sized the 3/8 copper correctly? I don't know but I would image it has a Taco pan-trol on the 1st. floor and high temp on 2nd. Any ideas/suggestions?Thanks Dave Palmer

Comments

  • Dale
    Dale Member Posts: 1,317
    interesting

    Heat loss is figured the same. If the persons were comfortable on the first floor what boiler temp was set. I think the ceiling needs to run at at least 140 degrees water so a condensing boiler may not be able to condense, a little cast iron should do the trick.
  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388
    looked

    at it today,2nd floor is convectors (always cold,owner says)
    can see all the piping in basement.It does have a old Taco Pan-trol on the system,I was thinking of seperating the 2nd floor off into its own zone.Running the 1st floor radiant thru a mixing valve,that way I could install a hot water maker and run the 2nd floor at a higher temp. sound okay? thanks Dave
  • hot_rod
    hot_rod Member Posts: 23,391
    How is the

    ceiling radiant installed? Generally any concrete, gypcrete, sheetrock, plaster, etc products handle 140F MAX. If this is a plaster installation I think you have a good idea in limiting the temperature to the ceiling radiant. Maybe even use a reset control that would modulate the temperature slowly, as opposed to a bang/ bang temperature control.

    Regardless, I still think you first step should be a heatloss calc. You need to get a base to work from.

    Ceiling radiant is a fairly powerful emitter seeing as they rarely have furniture or coverings, and nobody walks on them allowing a higher surface temperature :) You should be able to get some serious BTU/ square foot from that installation.


    As for the upper level, check the insulation value above that area, if possible. Blowing in some additional R value will offer a good payback and help you heat loss numbers.

    hot rod

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Robert O'Connor_3
    Robert O'Connor_3 Member Posts: 272
    What does it look like?

    Dave,

    How would I be able to tell that there's a radiant heat ceiling in a home without the homeowner telling me. In my case (I'm a home inspector) the home owner is often not available.

    And, how old is the house you're working on? How old is the radiant ceiling?

    From the wethead wannabe, Arlene
  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388
    it....

    seems to be gypcrete with a plaster finish,other ones in my area are concrete ceilings on wire mesh.Heat loss is 130,000,wanted to do oil fired with indirect and second floor high temp. and run mixing valve for radiant about 130*. sound ok ? thanks Dave Palmer
  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388


  • Dave Palmer_3
    Dave Palmer_3 Member Posts: 388
    first...

    if you don't see radiators,convectors or baseboard but you have a boiler that is the first clue. Then look around the main loop to see if there are 1/2 or 3/8 branches off of that disapearing up into the walls.Sometimes if the job was sloppy you can see tubing in the attic(peek under the insulation).The house is a small cape about 40 years old so the radiant is the same,no signs of leaks anywhere(yet);{
    but I told her don't be surpised if she see a spot or two in the future. Dave
  • Mark Hunt
    Mark Hunt Member Posts: 4,908
    Arlene


    Want me to bring some pics of old radiant ceilings in September?