Is is a good idea to change the water in boiler/radiators?
Joe.G
Member Posts: 213
I was wondering if I should drain the water from my boiler and radiators every few years or so,and refill if fresh water, what are the pros cons of this? Thanks
0
Comments
-
Maybe, maybe not
Is this a hot water system? Any non barrier tubing in the system?
Draw a glassful. How's it look? How's it smell?.
If you have a tight (non leaking) system, and you don't open it up, or add additional water, allowing fresh, oxygenated, possibly hard water into it, then.... You should be fine.
Not a bad idea to draw a fluid sample and have it tested ocassionally. Check your Yellow Pages for water treatment companies that can run the tests for you. Find one with boiler and cooling tower experience, as they know what to test for.
There are numerous hydronic conditioner chemicals that can adjust, or buffer your fluid, if needed.
hot rod
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yeah I have hot water in my boiler and radaitors, if I take the water out by the drain in the boiler it comes out black and smell nasty.0 -
Boiler needs cleaning
all that sludge may be blocking heat transfer, and this can shorten the life of the boiler. This is a job for a pro. Go to the Find a Contractor page of this site to find one near you.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
I can't just drain it at the boiler,open the auto feed and fill the system back up with water and bleed from teh top floor down? and then when I am done make sure the pressure is set at 12lb? thanks0 -
It will probably take
much more than that if the boiler has a lot of sludge. Simply draining it probably won't be enough. Also, depending on what boiler you have, it may be possible to damage it by improper cleaning techniques.
That's why I suggest you contact a pro.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Muck
will settle at the bottom so you drain off at the bottom and you should get maybe a shot of muck. If you drain the system and add fresh water, and with it oxygen, you'll only be starting the corrosion process all over. Drain a gallon and see if it clears up. If not or it really smells, bear in mind it's not supposed to smell fresh, call in a pro as the others said. It might be your water that's causing the problem in the first place. If your water has a high mineral content the same thing will happen again only this time it will be worse because you'll be adding oxygen when you refill.0 -
The drain for the boiler is at the bottom, the reason I am asking this ? I don't think it has ever been done, new water has been added when we moved some raditors but we dod not drain much, the water is balck and has a odor to it.0 -
It couldn't hurt
To have a cleaner run in the system, then flush and add a corrosion inhibitor. Some boiler guys use a 1% TSP solution to clean them out, some boiler installation manuals get into this procedure.
I prefer a hydronic system cleaner, a good flush, then refill with good fill water.
A squirt of conditioner is another good idea to protect the cleaned surfaces and maximize heat transfer. I use Rhomar brand cleaners and conditioners.
As Steam H mentioned, you may need a pro with a transfer pump and knowledge on how to assure all loops and zones have been cleaned and flushed adequatly.
www.rhomarwater.com
hot rodBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements