Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
One-Pipe System Thermostat-Controlled Air Vents
Bill Clumpner
Member Posts: 1
Presently involved with optimization of one-pipe steam system built in 1903. No drawings, no prints, no memory of where risers are or if there are air vents. Upper floors of five-floor building have heating problems. Most likely trapped air/non-condensibles. Am interested in finding out if one can effectively computer simulate/model steam energy efficiency improvements from installation of thermostat control valve between radiator and air vent to better manage air in the system. Any pitfalls to installing the valves? Are there any recommended manufacturers. Thanks.
0
Comments
-
Bill, the way to solve that problem
is by adding main-line air vents at the tops of those risers. One way to do this is shown in Dan's book "The Lost Art of Steam Heating" which you can order on the Books and More page of this site. Highly recommended.
If you can find out what pipe sizes are used in each riser, and how much length of each pipe size, the vent sizes can be figured mathematically. If not, trial and error will have to do.
With the steam mains in the basement properly vented, and the risers properly vented, each radiator will get steam at about the same time. Then you can add TRVs to serve as limiters.
Where is this job located? We have plenty of steam men here who can help you- go to the Find a Contractor page of this site. If you're in or near Baltimore, e-mail me!
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements