Pilot Duty Rating

Mark J Strawcutter
Member Posts: 625
I'm looking for the definition/meaning of the "pilot duty" rating of relays and the like.
Mark
Mark
0
Comments
-
Public info from Rockwell
Question:
For relay contacts, why is there sometimes a difference in Rated Thermal Current and the Thermal Continuous Current Test from the NEMA Contact Ratings Designation for Pilot Duty Ratings?
Answer:
For example, we can review the Electrical Ratings on the 700-HA relays:
The 10A thermal current is both an IEC and UL rating. The 10A rating for UL is termed "general purpose" which is a slightly inductive load. The B300 rating is termed "pilot duty" which means it is for a specific highly inductive load. UL / NEMA define the B300 thermal current as 5A and this does not change even if the product can support a higher thermal current. All of the A-B relays have a general purpose rating and most have a pilot duty rating. This means that a 700-HA for example has a thermal rating of 10A and is also capable of switching inductive loads as described by B300.0 -
Pilot Duty
In simple terms it defines for some switching contacts on controls their diversity of voltage applications.
Example: A series 40 120 volt control such as a P404 pressuretrol used on many older steam systems can be used for 120 volts, 24 volts and millivolts. They are often called Dual Rated Controls, they may have a rating that says PILOT DUTY 2 a at 25 VAC; 0.25 A at .25 to 12 VDC this would mean a control could be used on 24 volts and also millivolts (750 millivolts is 3/4 of a volt DC).
0
This discussion has been closed.
Categories
- All Categories
- 86.9K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 57 Biomass
- 425 Carbon Monoxide Awareness
- 109 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.6K Gas Heating
- 105 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 70 Pipe Deterioration
- 969 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 44 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements