Injection pumping
JoeP
Member Posts: 4
New to radiant & injection pumping...
Installing a system that will have 5 radiant zones, 1 hi-temp copper baseboard, and indirect DHW. Three of the radiant zones are designed for same supply temperature. Does this mean I can have just 3 injection pumps-one for all 3 zones of same temp, and the other two?
Installing a system that will have 5 radiant zones, 1 hi-temp copper baseboard, and indirect DHW. Three of the radiant zones are designed for same supply temperature. Does this mean I can have just 3 injection pumps-one for all 3 zones of same temp, and the other two?
0
Comments
-
If the other two
are designed for the same temperature or reset ratio, then you'll have:
Injection system #1: 3 zones radiant
Injection system #2: 2 zones radiant
Injection system #3: baseboard
It's too bad the Munchkin Vision II control is not available yet since this is exactly what it's meant to do, i.e. multiple temperature zoning w/ outdoor reset.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Injection
Check out Wirsbo and or techmar controls they have exactly what you are looking for including clear piping diagrams.
John0 -
tekmar 363
Check out tekmar's 363 control, this control has all you
will need. Excellent piping and wiring diagrams to chose from. We hooked up a light bulb in series 120v to the injection pump from the tekmar, just for fun, was neat to watch. Good Luck
www.tekmarcontrols.com
0 -
tekmar 363
Check out tekmar's 363 control, this control has all you
will need. Excellent piping and wiring diagrams to chose from. We hooked up a light bulb in series 120v to the injection pump from the tekmar, just for fun, was neat to watch. Good Luck
www.tekmarcontrols.com
0 -
Three temp system.
Take a look at the attached pdf file.
It show your two hi temp zones (BB and Indirect) Injection for radiant and then a manual mixing valve for the other radiant temp.Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -
or a 371?
This thread:
http://forums.invision.net/Thread.cfm?CFApp=2&&Message_ID=38557
Has some pictures and description of a great looking system by Boilerpro using a Tekmar 371 that does just about what you want. It has two lower temps off of one injection controller but could easily be modified for three.0 -
Give me a call
Call me on Monday and I will help you design this system. I can shoiw you how to figure out the flows(injection rates) pump selection, pipe sizing, etc. We can then come up with piping and wiring diagram.
952-997-5334
Tim D.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements