Injection pumping

JoeP
JoeP Member Posts: 4
New to radiant & injection pumping...
Installing a system that will have 5 radiant zones, 1 hi-temp copper baseboard, and indirect DHW. Three of the radiant zones are designed for same supply temperature. Does this mean I can have just 3 injection pumps-one for all 3 zones of same temp, and the other two?

Comments

  • If the other two

    are designed for the same temperature or reset ratio, then you'll have:

    Injection system #1: 3 zones radiant

    Injection system #2: 2 zones radiant

    Injection system #3: baseboard

    It's too bad the Munchkin Vision II control is not available yet since this is exactly what it's meant to do, i.e. multiple temperature zoning w/ outdoor reset.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • John Abbott
    John Abbott Member Posts: 358
    Injection

    Check out Wirsbo and or techmar controls they have exactly what you are looking for including clear piping diagrams.

    John
  • Bart
    Bart Member Posts: 14
    tekmar 363

    Check out tekmar's 363 control, this control has all you
    will need. Excellent piping and wiring diagrams to chose from. We hooked up a light bulb in series 120v to the injection pump from the tekmar, just for fun, was neat to watch. Good Luck
    www.tekmarcontrols.com


  • Bart
    Bart Member Posts: 14
    tekmar 363

    Check out tekmar's 363 control, this control has all you
    will need. Excellent piping and wiring diagrams to chose from. We hooked up a light bulb in series 120v to the injection pump from the tekmar, just for fun, was neat to watch. Good Luck
    www.tekmarcontrols.com


  • Dave H_2
    Dave H_2 Member Posts: 594
    Three temp system.

    Take a look at the attached pdf file.

    It show your two hi temp zones (BB and Indirect) Injection for radiant and then a manual mixing valve for the other radiant temp.

    Dave Holdorf

    Technical Training Manager - East

    Taco Comfort Solutions

  • Dan_8
    Dan_8 Member Posts: 56
    or a 371?

    This thread:

    http://forums.invision.net/Thread.cfm?CFApp=2&&Message_ID=38557

    Has some pictures and description of a great looking system by Boilerpro using a Tekmar 371 that does just about what you want. It has two lower temps off of one injection controller but could easily be modified for three.
  • Tim Doran_2
    Tim Doran_2 Member Posts: 131
    Give me a call

    Call me on Monday and I will help you design this system. I can shoiw you how to figure out the flows(injection rates) pump selection, pipe sizing, etc. We can then come up with piping and wiring diagram.