one or two risers?, Weil-McLain

Steve Todd
Steve Todd Member Posts: 6
Hello. I need to replace the near-boiler leaking-copper (ack) piping on my home's Weil-McLain PEG-50; getting quotes for this work with this site's Find-a-Contractor (great service).

When I look at Weil-McLain's own manual/product literature, one source seems to spec a single (1) 2.5" riser (as a minimum recommended pipe size), while a second source specs two (2) 2.5" risers.

First question: Is it that one 2.5" is the bare minimum, while two 2.5" (or 3") the better thing to do (to lower the steam velocity)?
(fyi, the boiler currently has one riser.)

And second question: Would a dropped-header be going overboard?

Thank you very much.

Comments

  • you're on the right track

    With steam, and anyone's boiler, more is better on the risers and size of them.

    A dropped header is needed when there isn't height enough for the risers as specified by the Manufacturer.

    They can be used on every boiler, without harm. A dropped header makes connecting the risers much easier, as it adds a swing joint to each riser. It saves enough labor to be worth it without any added cost.

    I don't know what the minimum is for that boiler, I know that was the original question.

    Noel
  • Al Letellier
    Al Letellier Member Posts: 781
    W/M PEG 50

    Steve, the install manual for all EG boilers shows a single 2 1/2" riser, a 2 1/2" header and an 1 1/2" equalizer. You don't need 2 risers until the 85-95 size.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Mad Dog
    Mad Dog Member Posts: 2,595
    No, you Don't but it will only improve

    the quality of the steam. It really depends...a small steam boiler We'll use one riser sometimes, but go either 2 1/2" and in many cases 3" Mad Dog

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Steamhead
    Steamhead Member Posts: 17,492
    Steve, if that boiler has two supply tappings

    I'd use two risers to the header. And if you don't have enough headroom, a drop header is the solution. Here's one of my favorites- Mad Dog's turn this time.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Yep , like Noel says

    Using a drop header makes connecting the 2 risers much easier , and it only cost us 2 street ells . This was our first try at a drop header , and its my preferred method since .

    With using the 2nd supply , like others said , it can only help in producing dry steam , slowing the velocity out of the boiler . It always depends on if you have the room and the time . See if you can post some pics of the job when its done , good luck Steve .
  • TJ_2
    TJ_2 Member Posts: 26
    W-M PEG 50

    My PEG 50 manual (1997) specifies a single 3" riser. That's how mine was installed and it works very well.
  • Steve Todd
    Steve Todd Member Posts: 6
    Thank you

    Thank you all for your input and guidance.
    I'll take before & after pictures and post later this summer.