Head loss in cast iron radiators
MDineen
Member Posts: 1
does anyone have information on how to calculate head loss on cast iron radiators?
0
Comments
-
Nil...
Zip... Nada...Zero.
Especially if you flow it at the delta T it was originally designed for, 30 to 40 degrees. Even if you double the flow rate, 3-1/3 times zero is still zero.
Oh yeah, did I mention the valves had to be wide open and there shouldn't be any orifices in the radiator piping?
Zero.
ME0