Black or Galvanized?
Pete Novak
Member Posts: 23
I'm ready to purchase the pipe for a single pipe steam return that runs under/through a concrete slab. The old is out, and the new is ready to go in. Two questions:
1. Do I buy black or galvanized pipe for this project? It is 1-1/4" pipe. I can't tell what the old stuff is. It's rusted.
2. There are two lines from opposite sides of the room that run to the center of the room. Then they merge into one perpendicular line and continue on to the boiler. The old installation had them installed with an offset T design to eliminate water hammer. Should I reinstall an offset T design or is there a suitable Y pipe to use? I can post a drawing if needed.
Thanks - Pete
1. Do I buy black or galvanized pipe for this project? It is 1-1/4" pipe. I can't tell what the old stuff is. It's rusted.
2. There are two lines from opposite sides of the room that run to the center of the room. Then they merge into one perpendicular line and continue on to the boiler. The old installation had them installed with an offset T design to eliminate water hammer. Should I reinstall an offset T design or is there a suitable Y pipe to use? I can post a drawing if needed.
Thanks - Pete
0
Comments
-
Go with black
post a pic if ya can. Mad Dog
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
i thought that...
it was taboo to use Galvy on steam because of the zinc flaking off and cousing all kinds of problems...kpc0 -
drawing of return pipe layout
Here's a simple drawing of the return pipe layout. It's bird's eye view of the radiator's and return pipes. The one on the left is what was the original off-set T design, and the one one on the right is the proposed Y design. What do you think? Thanks Pete
0 -
drawing of return pipe layout
Here's a simple drawing of the return pipe layout. It's bird's eye view of the radiator's and return pipes. The one on the left is what was the original off-set T design, and the one one on the right is the proposed Y design. I can send it as a tiff or jpeg if needed. What do you think? Thanks Pete0 -
it
won't open for me!!!
jpeg works better most of the time
Chris0 -
Have to have word to open doc.
0 -
here's the jpeg
0 -
Pete
Is there any way you can tee the 2 return lines lower ? With a tee or a Y that high , theres always a chance of steam hitting returning condensate from the other return . If you can tee them below the normal water line of the boiler you can eliminate that problem , and it won't matter what you use - tee , Y - they both work well on a gravity return . And what KPC said about using galvanized is what I've heard , it can flake off and cause some problems . Go with black steel . Good luck .0 -
The rule of thumb is
Black steel typically averages 40 year life under normal underground circumstances. Less if the soil is corrosive or wet, more if factors are good. If you are concerned, there are pipe wrapping materials that can be had from most any pipe supply place, or, I've seen people simply tar the pipe thoroughly once it's in place and bury it.0 -
ok. I'm going w/ the black
Thanks for the help. I'm going with the black. I should have most of it installed tomorrow.
0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements