steam system

Geno_2
Geno_2 Member Posts: 8
I agree with Al. A 1200 sq. ft. addition is large and will require a heat load calculation to see if your system can handle it. Is it several rooms?, a great room?, how much glass?,ceiling height, etc, etc. Do your self a favor, talk to a contractor in your area.
Geno

Comments

  • shawn_3
    shawn_3 Member Posts: 20
    staem

    I am doing a addition on a house where the existing house is steam. I would like to know if it possible to run a loop of baseboard off the bottom of the boiler.and how to pipe that.or is it best to just put a seperate boiler to heat about 1200 sq feet of space and answers would help.
  • Al Letellier
    Al Letellier Member Posts: 781
    steam system add on zone

    It's possible to do,Shawn, but you need to be careful about how you go about it.First, you're dealing with water a lot hottter that 180 when tapping off the bottom of a steam boiler, and you have to account for that in your planning.
    If you're considering a separate boiler and the extra cost of one, it may be wise to consider upgrading the whole system.
    If you're not a contractor, go to the find a contractor portion of this site and get some professional help. This kind of job is not for the DIY-fer.
    Good luck.

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • steve_6
    steve_6 Member Posts: 243
    hot water zone

    check out "like to run a hot water zone off a steam boiler" under hot tech topics on this web sight
  • Steamhead
    Steamhead Member Posts: 17,492
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting