Ground source Heat pumps and radiant/airhandlers

Bryan_16
Bryan_16 Member Posts: 262
I can get water hot enough to do a radiant slab[120F], but how can I get my water to 180F for an air handler? What happens if I run the 120F water through the coil, take what I get for temp rise and add electric resisant as 2nd stage? Cost of operation will go up. How much? Any ideas would be appreciated.

Bryan

Comments

  • Paul_6
    Paul_6 Member Posts: 88
    Derate your coil for a

    lower water temperature. We have heated comercial jobs just fine with 125° water, without supplemental heat. Some heat pumps will put out 140° water with out any additional modification. Paul
  • This content has been removed.
  • Bryan_16
    Bryan_16 Member Posts: 262
    gshp

    Heat loss has been done. GSHP will be used to heeat garage slab, basement floor and make hot water for two air handlers. Tubing will be at bottom of 4" thick slab. Unit is ECONAR GW098. E-mail if you want more info. Thank you for the help. Bryan
  • Bryan_16
    Bryan_16 Member Posts: 262
    forgot

    > Heat loss has been done. GSHP will be used to

    > heeat garage slab, basement floor and make hot

    > water for two air handlers. Tubing will be at

    > bottom of 4" thick slab. Unit is ECONAR GW098.

    > E-mail if you want more info. Thank you for the

    > help. Bryan



  • Bryan_16
    Bryan_16 Member Posts: 262
    forgot

    I am in SE South Dakota