Ground source Heat pumps and radiant/airhandlers
Bryan_16
Member Posts: 262
I can get water hot enough to do a radiant slab[120F], but how can I get my water to 180F for an air handler? What happens if I run the 120F water through the coil, take what I get for temp rise and add electric resisant as 2nd stage? Cost of operation will go up. How much? Any ideas would be appreciated.
Bryan
Bryan
0
Comments
-
Derate your coil for a
lower water temperature. We have heated comercial jobs just fine with 125° water, without supplemental heat. Some heat pumps will put out 140° water with out any additional modification. Paul0 -
This content has been removed.
-
gshp
Heat loss has been done. GSHP will be used to heeat garage slab, basement floor and make hot water for two air handlers. Tubing will be at bottom of 4" thick slab. Unit is ECONAR GW098. E-mail if you want more info. Thank you for the help. Bryan0 -
forgot
> Heat loss has been done. GSHP will be used to
> heeat garage slab, basement floor and make hot
> water for two air handlers. Tubing will be at
> bottom of 4" thick slab. Unit is ECONAR GW098.
> E-mail if you want more info. Thank you for the
> help. Bryan
0 -
forgot
I am in SE South Dakota0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements