Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Stem Boiler Sizing
Wayne_14
Member Posts: 39
Need to replace a steam boiler, once we have the square feet with a lot of help from "Dan's" book, what is the multiplier or safety factor needed.
0
Comments
-
steam boiler sizing
Wayne, most of todays boiler manufacturers factor pick-up load in their sizing. If your mains are insulated, size the boiler to the connected load, if not, check with the boiler manufacturer to be sure. Page 75 of "lost art of steam heating" gives a good explanation of haw to size when in doubt.
Good luck.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
Thank You
I have to "BORROW" back my book.0 -
Steam Boiler sizing
The PMAA manual recomends that you add up the EDR of all radiators. Then multiply by a pick up factor of 1.33.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements