Help sizing equipment
Joh n Brickey
Member Posts: 43
I,m trying to size the equipment in a new house. It has in floor heat and I would like to know how to size this for an indirect fired water heater off of the same boiler. My heat load is 89,000 btu. the house has 3 full bathrooms,2 half baths,a dishwasher and the master bath has a whirlpool and a 6x6 shower with body sprays. I'd like to try the Munchkin boiler and their IDF water heater. Any help would be appreceiated. Thanks!
0
Comments
-
Munchkin
with the Vision 1 control prioritizes the DHW, so do not add that into your heat load.
I would use an SSU-40.
Mark H
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0 -
sizing equipment
Many variable to consider here. But first and foremost, what is the volume of the whirlpool? With a small boiler, you may need added volumne and the indirect should have at least the capacity of the tub. Also, most spa faucet deliver a lot of water. A five head spa can deliver 13 gallons a minute. Get the info together and consult a plumbing or heating pro. Don't get left short on hot water.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements