We have a job in San Francisco where quite a few of the existing steam radiators will now be oversized because the rooms will be insulated and the windows changed to double glazed. What experience have you with the Danfoss RA 2000 for steam radiators as far as reliability and performance?

I'm told that you have to cycle the boiler with a timer; like on-off every 20 minutes or so to give the radiator a chance to fill up with air again so that the TRV can close if it's reached setpoint.

Mad Dog, Steamhead, Mark Hunt, etc.; are you there?

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=53&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Unknown
    Options
    They work well

    Put the thermostat in a room that has no trv, usually a cooler room, and let 'er rip! You'll be very happy.

    Noel
  • Mad Dog
    Mad Dog Member Posts: 2,595
    Options
    Good advice from Noel as usual

    also, yes, it is critical that the boiler does not run all the time...had a commercial job once, where the boioler ran 24 /7 ...trvs could not hold back a thing....but this is an odd job...on resiedential i wouldn't worry. md

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Alaska Joe
    Alaska Joe Member Posts: 37
    Options
    What pressure steam

    Kind of curious what pressure steam you were running? TRV's installed on my larger buildings,(300 man soldier dorms)baseboard type DanFoss valves, I believe 2000's, no problem when they remodeled all the windows. Had steam PRV's that maintained the 7 to 11 pound range. I thought proportional meant that it was always seeking, unless the TRV is turned to the off position.... Joe
  • Steamhead
    Steamhead Member Posts: 16,879
    Options
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • DWood
    DWood Member Posts: 60
    Options
    Boiler Cycling

    Alan,
    The only time you "need" to cycle the boiler with a Danfoss TRV is when using the 1 pipe steam valve. With this valve we are controling the release of air from the system and need the system to go to zero pressure at least once an hour to allow air back into the system. These valves work well to prevent overheating and best when used with systems operating on ounces of pressure, not pounds.
    Good luck,
    DWood
  • Alan(CaliforniaRadiant)Forbes
    Options
    Thanks, guys

    This system operates at 2 psi.

    How long can the owner expect these TRV's to last? 2 yrs., 10 yrs., more?

    Alan

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Unknown
    Options
    More

    In my experience, at a college with 800 of them, mostly on steam, they only fail when physically assaulted.

    I used Macon, Taco, Honeywell/Braukman, Danfoss, and Tour and Andersen.

    They hold up well.

    Noel