Circulator Sizing
Can anyone help me out with sizing a circulator for a primary circuit in a primary/secondary piping system? The secondary systems are all zoned with circulators. Do I need to size for all the flow rates in every secondary circuit or just a portion of the flow?
Thanks for the help,
Dave Bennett
  • David A. Bennett
    David A. Bennett Member Posts: 2
    Circulator Sizing
    Dave Bennett
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,732
    You need to size
    for the total load, but at a temperature drop that's determined by the sum of what the secondary circuits will be doing.
    You might want to get this book:
    http://www.heatinghelp.com/shopcart/product.cfm?category=2-44
    Retired and loving it.