Heat exchanger
Bill Barrett
Member Posts: 43
Just playing in the shop. Does anyone has a formula that would give me a close idea of BTU transfer, if we have all the variables such as, surface area of material ,type of material, delta T, gpm, etc. Thanks
0
Comments
-
0
-
Here's The One I Use
Q = UA(LMTD)
Q = BTU/hr
U = heat transfer coefficient
A = surface area in square feet
LMTD = log of the mean temperature difference
The heat transfer coefficient varies with the type of HX. It's kind of where art meets science. Shell & tubes will run 100 to 300, while plates, and shell & coil will be in the 650 - 1000 range, depending.
The LMTD is a pain to calculate long hand, but I've got a nomograph, or a little spreadsheet, and can easily do it for you if you give me the inlet and outlet temperatures for both the hot and cold sides of the HX.
Material type really doesn't make a huge difference for most applications. There are other factors that can come into play, like baffles in a shell & tube design, pressure drop across both sides of the HX, nozzle sizes, etc.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements