Taco IFC circs

Dan Peel
Dan Peel Member Posts: 431
The tubing is black 3/4 Kitec feeding a remote manifold. It's a constant flow setup and the zone valve is a 3-way Taco. Dan

<A HREF="http://www.heatinghelp.com/getListed.cfm?id=174&Step=30">To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"</A>

Comments

  • Dan Peel
    Dan Peel Member Posts: 431
    Flipping flanges

    I finally bought a few 007s with the internal flow check. They rotated the flanges to match most of the rest of the market. I'll keep an extra in the truck! Dan

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • James_2
    James_2 Member Posts: 24
    Taco Pumps

    Taco actually offers both configurations. I have noticed various models have different configurations in the brochures. Both configurations have an advantage.
  • Joe_30
    Joe_30 Member Posts: 85
    Same size??

    Are these Taco-with- flow-checks the exact same length as those without flowchecks, so that they can drop in replace them.??
  • Dan Peel
    Dan Peel Member Posts: 431
    Flange to flange

    The lengths are the same. They are physically taller. Unlike the Grundfos where the flow check is inserted at the outlet, Taco have placed it above the eye of the impeller. DP

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Tom M.
    Tom M. Member Posts: 237
    Flange orientation

    The 007 that comes with an Amtrol has this configuration. I think it is better suited to being mounted on a horizontal pipe. I think that the flanges that are parallel to the axis of the pump make it convenient to replace an inline circulator, such as a 110, which had the flanges this way to support the weight of the motor when mounted on a vertical pipe. I'm not an authority on the subject, just thinking out loud.
    Tom M.
  • Tony_8
    Tony_8 Member Posts: 608
    IFC 007

    I use these almost exclusively and won't go back to flow-checks. Just be careful of air-locking the circ motor as it is easy to do.
  • Dan Peel
    Dan Peel Member Posts: 431
    How tough?

    Tony, are they harder to clear initially or do they trap air later? DP

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Tony_8
    Tony_8 Member Posts: 608
    usually

    initially but have had some lock up later on systems with loops lower than circ and/or w/scoops or inadequate air elim equip. Taco recommends a purge valve downstream. I use iso-flanges and "crack" the flange on the outlet side. Haven't had any problem with systems using Spirovent after initial fill up. Found that if you pressurize the loop from the circ side 1st it usually purges the circ.
  • hot_rod
    hot_rod Member Posts: 23,828
    I've always

    been trained that putting a flow restricting device at the impeller like that invites cavatation, and air bound circs? Seems like it's trading a flow check solution for an air bound impeller potential. Shine the light for me, someone:)

    hot rod
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • kevin
    kevin Member Posts: 420
    what type....

    of tubing is that coming out of the circs.? What set up is thw ZV and the circ on the same run for? I must be too close to see what is really going on... tia kpc
  • Boilerpro_3
    Boilerpro_3 Member Posts: 1,231
    I'm with you, HR

    Sounds like a design that invites trouble. With these high head, low flow circs often used in very small zones, I think there are going to be some headaches with this.

    Boilerpro