What is the proper spacing for closely spaced tee's
Mike202
Member Posts: 1
What is the proper spacing for closely spaced tee's for 1" branches off 2" main?
0
Comments
-
as close as possible
but not more than 12"Retired and loving it.0 -
I think
The rule of thumb is no more than 4 pipe diameters apart. Example: If your main loop is 2" it would be 8". Like Dan said, the closer the better. Use the 4 diameter rule as a worst case.0 -
between sets
isn't there also a minimum distance between the return from one set and the supply from the next set?
Mark0 -
No, there isn't
At least not that I've ever heard of, Mark. The goal is to eliminate pressure drop in the common piping. Each circuit stands on its own once you've done that and spacing between circuits shouldn't be an issue.Retired and loving it.0 -
I found it
Here's a posting from the wall a while back:
>Date: January 20, 2003 11:55 PM
>Author: Gary Wilson (gary@wilsonph.com)
>Subject: One more tip
>I went to the Holohan school of Primary/Secondary. Please
>excuse me if I'm wrong, but isn't there supossed to be 8
>pipe diameters between the sets of take-offs? One space
>saving tip is to run a batch of secondaries off of the
>lower header, and just offset around the upper group. Then
>again, if you have the room, it does look sweet the way
>you have it.
Nobody ever disagreed so I assumed it was correct :-)
Mark0 -
That applies
only where the secondary flow is greater than the primary flow.Retired and loving it.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements