Size of pipes in forced water heating system
Bill de Rosa
Member Posts: 3
Thank you again. I find your replies very helpful.
As you have been so kind I would like to take further advantage of it.
What are the balance considerations which come into play?? Also is there a place, like the one you gave me for the gravity system, where I can learn the basics of a forced water system?? I have quite a few questions that come to mind, such as circulator type and size, kind of pipe material (i.e. iron vs copper) and so on.
For what professionals are concerned, I am quite discouraged, that is the reason I am attempting to learn as much as I can. It seems that everybody is interested in changing the boiler, but nobody wants to mess with the plumbing. I have had three H/C companies look at the system; they all gave me different answers, nobody even mentioned what, after following your suggestion and reading about the gravity system, seems a quite obvious thing: I have a system converted from "gravity" to "forced". I apologize for venting my frustration, but I was trying to explain why I am attempting to learn as much as I possibly can.
Than you again.
As you have been so kind I would like to take further advantage of it.
What are the balance considerations which come into play?? Also is there a place, like the one you gave me for the gravity system, where I can learn the basics of a forced water system?? I have quite a few questions that come to mind, such as circulator type and size, kind of pipe material (i.e. iron vs copper) and so on.
For what professionals are concerned, I am quite discouraged, that is the reason I am attempting to learn as much as I can. It seems that everybody is interested in changing the boiler, but nobody wants to mess with the plumbing. I have had three H/C companies look at the system; they all gave me different answers, nobody even mentioned what, after following your suggestion and reading about the gravity system, seems a quite obvious thing: I have a system converted from "gravity" to "forced". I apologize for venting my frustration, but I was trying to explain why I am attempting to learn as much as I possibly can.
Than you again.
0
Comments
-
Pipe sizes in forced water hydronic system
I need some help!! I am refinishing the basement in an old brick building with forced water heating system. The building is two floors high on top of a good height basement. The pipes (cast iron) carrying the water from the boiler start at 3/4 at the boiler and increase to 3 to 4 inches along the basement ceiling, before being reduced again to 3/4 as they start rising toward the first and second floor. The return pipes enter the basement at 3/4 and expand to 3 4 inches along the ceiling before being reduced to 3/4 at the boiler return manifold. What is the function (if any) of such large pipes?? I would like to change them with 1" pipes so I can gain some head space. If I do that will there be enough heat still carried to the first and second floor??
Thank you in advance for your ideas.0 -
Sound like
you have an old gravity hot water system. You can read all about it here (cut and paste)
http://www.heatinghelp.com/heating_howcome1.cfmRetired and loving it.0 -
Thank you for your reply. I have followed your suggestion and read about the gravity system. It gives suggestions on how to replace near-boiler pipes.
My question is: can I change all the pipes running along the basement ceiling using the same formulas without interfering with (and eventually improving) the heating efficiency of the system??
Thank you0 -
Those rule
apply to the near-boiler piping. You can reduce the size of your basement pipes if your system has a circulator, but the size would be based on the flow rate, which is based on the heat loss. One-inch pipe, for instance, has a maximum flow rate of 8 gallons per minute. Based on a 20-degree temperature drop across the system, that represents 80,000 BTUs per hour, which is quite a bit.
If you're not comfortable with the sizing, it would be best to have a pro look it over and make recommendations. There's also the issue of system balance to consider.
Thanks for the good question.Retired and loving it.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements