hot tub
shawn_3
Member Posts: 20
I recently recieved a job a to do some heat and plumbing and the contractor asked me to look at the hot tub it is was cut off in some areas it looks like it was connected to the tankless seperately it then is run over to the pumps and filter etc. it has a zone valve on the line too and a operating control which is connected into the 2 inch pvc line for the pump.never seen this before to me it looks like when you hit the pressure switch for the pump it circulates through there any ideas on how to pipe this do i need a mixing valve any ideas would really help thank you
0
Comments
-
hot tub piping
Shawn, I'm not sure of the piping arrangement you're describing, but here's how we've done it. Superstor makes a great little 20 indirect pool heater. Pipe it like an indirect on the boiler side, but install a bypass to help with cold start up. Once the tub is heated, you won't need the bypass. On the pool side, pipe the pump discharge into the tank and out again to the filter. Install a bypass here too and use a ball valve to throttle the flow so only some of the water gets heated at a time, not all of it.
You can use a small heat exchanger as well to do the job, We have 2 of these little tanks on several jobs. One heats a 20x40 pool from 40 degrees up to 80 in about 3 days with a 100,000 BTU boiler, and it heats a 150 gallon hot tub as well off a separate heat tank. Total fuel consumption is about 300 gallons of oil a season.
Basic explanation, but SuperStor has a good diagram to follow for this type of installation....works great.
To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements