Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

oversized boiler

Boilerpro_3
Boilerpro_3 Member Posts: 1,231
I believe most Raypacks were available from the factory with modulating gas valves and burners designed to allow downfiring to between 20% to 50% of maximum input. Probably one of the best copper tube boilers out there that I've seen.

Boilerpro

Comments

  • Joe Furfaro
    Joe Furfaro Member Posts: 30
    Oversized boiler

    I had a new boiler installed last year when I moved into my home. The contractor just replaced it with the same model and size. This past winter it sometimes seemed that the boiler would turn on and off every five minutes. I had a heat loss done and it came in at 90,000 btu. The boiler is 165,000 btu. I would appreciate any suggestions.
    Thanks
  • heatboy
    heatboy Member Posts: 1,468
    Was the heat loss........

    done before or after the boiler was replaced?

    hb

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"

    There was an error rendering this rich post.

  • Al Letellier
    Al Letellier Member Posts: 781
    oversized boiler

    You wouldn't believe how often this happens. Sad to say but true. Your options are limited here. You can downfire the nozzle or you can downsize the boiler. You didn't say steam or hot water heat or what type of boiler you have, so it's hard to give solid advise here, so here it comes again.....find a competent heating professional and have him determine your best option.
    Some boilers are easy to take apart and make smaller, some not. Downfiring is way easier and less xpensive but has to be done right. Get a pro to help!!!

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
  • Joe Furfaro
    Joe Furfaro Member Posts: 30


    Thanks for the advice. The heat loss was just done recently.
    The boiler is a Raypak model. Hot Water.
    I will contact a professional.
  • Steamhead
    Steamhead Member Posts: 17,490
    Joe, try the Find a Contractor page

    on this site. If you're in the Baltimore area, e-mail me!

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • heatboy
    heatboy Member Posts: 1,468
    Well, looks like you have ......

    three choices:

    1. Replace the boiler with one that is sized correctly.

    2. Build an addition to your house.

    3. Sell some energy to you neighbors.

    Down firing your current boiler isn't really an option because you can't downfire it enough without causing other issues that are worse than your current ones. This happens far more often than it ever should. With all of the computer based sizing programs available, it is unacceptable to have heating/cooling work done without performing these. Any serious heating professional will do this before ever starting the project. I'm very sorry this has happened to you.

    hb

    To Learn More About This Contractor, Click Here to Visit Their Ad in "Find A Contractor"

    There was an error rendering this rich post.

  • sootmonkey
    sootmonkey Member Posts: 158
    H2O demand

    You didn't say how you get your hot water. How many baths do you have? I have found that many systems are designed for the hot water load. It may be that you need a system that big to supply the hot water.
  • Jackchips
    Jackchips Member Posts: 344
    If your

    not supplying your hot water you could look into adding a super store for the winter and using the water heater when you turn your heat off.
  • Steve Miller
    Steve Miller Member Posts: 115
    Buffer tank

    With a Raypak low mass boiler a buffer tank is always a good idea. You can then use outdoor reset off the tank for better efficiencies. This can solve flow issues associated with low mass boiler as well. Raypak makes a pretty nice buffer tank too and you can get them custom made with whatever tap size you need. Good luck!

    Steve M.
  • joel_4
    joel_4 Member Posts: 42
    sootmonkey

    While boilers are upsized all the time for hot water load in most cases this is a mistake. A better approach is to install a larger indirect tank instead. That way the boiler can be sized for the true biulding load. Of course you can't apply that to say the locker room at the locale Gold's gym but for houses it typically works just fine